fcflores1 Posted April 5, 2007 Report Posted April 5, 2007 Hey Guys, How does one calculate motor fusing requirements? I would like to fuse before the starter and at the main disconnect. (10 ft away) Example: 3 HP Motor: 460 (480) Volts: 4.8 FLA: Would I take 4.8 * 120%? (Before motor starter) Would I take 4.8 * 150%? (At the Disconnect) How does one calculate disconnect fusing with 5 motors. (Using above example) "You definitely want to add all of the MAX amps for a total full load rating. That becomes the worst case scenario. Then add 10 to 50% for heat de-rating. Your local code should be consulted for the exact amount of de-rating based on length of the cable run" "For panels with motor loads you typically take the motor with the largest current draw and multiply it by 125%, then add all of the other motor loads to that for a total (of motors only). Then add in other loads such as transformers, etc." Are the above statements correct? Quote
GerryM Posted April 9, 2007 Report Posted April 9, 2007 First go to here and look at table 430.52 for the fuse size range, as well as the whole 430 section. NEC Each motor fuse if not Design B looks like 175% x 4.8 = 8.4 (next higher fuse is allowed, probably 9A) max. dual element fuse for each For the feeder see Example D8 in the NEC under Appendix D and 430.62. For you thats 9A + (4.8 x 4) = 28.2A (next lower fuse is used, probably 25A) Statement 1: It depends, I'm not sure exactly what this refers to. Your cable length of 10' isn;t long enough to worry about derating. There is a derating for more than 3 current carrying conductors in a conduit, see Table 310.15(B)(2)(a). Statement 2: That is for the calculation of a panel main. Quote
fcflores1 Posted April 10, 2007 Author Report Posted April 10, 2007 How would I properly fuse at the disconnet; for one motor? 8.4+4.8=13.2???? Quote
GerryM Posted April 10, 2007 Report Posted April 10, 2007 9A max. for a dual element fuse for one. Quote
fcflores1 Posted April 10, 2007 Author Report Posted April 10, 2007 So let me get this straight. I would fuse each leg before the motor starter with 9 amp fuses. And since i using a disconnect bus drop that is fused i should use the same size fuse? Quote
fcflores1 Posted April 10, 2007 Author Report Posted April 10, 2007 (edited) Could you tell me if I am on the right path. Motor Name plate: 15 hp Motor 208 Volt 37.5 Amps FLA Panel Fuse: Time Delay fuse 37.5A x 175%= 65.625Amp Buss box fuse: Time Delay fuse 37.5A x 175%=65.625Amp Wire size in panel: #6 37.5x120%=45 amps Wire size going to Buss box: 140 ft x (37.5x120%) amps x 1= 6300 5.5 x 1000000/6300= 873.016 Wire size at 80% power factor= #6 Conduit size 1 inch EMT Overload device: Thermal/Magnetic 37.5x115%=43.125 Amps Edited April 18, 2007 by fcflores1 Quote
GerryM Posted April 11, 2007 Report Posted April 11, 2007 You can use this website to check your calculations. And don't forget to read the NEC, that's where it all comes from. http://www.electrician2.com/calculators/motor_ver_1.html The fuse and wire size is based on the table in the NEC not the motor nameplate. Only the OL setting is determined from the nameplate amps. Use 125%, not 120%. I don't follow your voltage drop calculation, but yes #6 should be fine in a 1" conduit. 175% + next standard size is the max. fuse you can use. I usually use 125%x FLA with a nice bussmann low peak fuse with no problems. Quote
gravitar Posted April 11, 2007 Report Posted April 11, 2007 Wow, great website! Lots of great information there that I'm looking forward to reading. Have you seen his "gallery" of electrical burn pictures? Those have to be the most horrifying images I have ever seen, and bring it all into perspective as to why we have all these rules and regulations to follow. Quote
GerryM Posted April 11, 2007 Report Posted April 11, 2007 Yes, there are lots of great calculators and articles. The burn stuff I've seen too many times now from electrical safety training. Its the best thing to use to convince people to use there PPE for sure. The last slide show I saw was a time elapse of a guys electrocuted leg over the course of a few days. It got really disgusting just before they amputed it. But it worked on me anyway, i'm a PPE believer now. Quote
denizen360 Posted September 20, 2011 Report Posted September 20, 2011 Somewhat it is ok.. full load current chart will help you to make rite decision..full load current Quote
Recommended Posts
Join the conversation
You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.