ParaffinPower Posted March 9, 2008 Report Posted March 9, 2008 View File CP1L and CP1H EasyModbus FB Ideally suited to multiple Omron inverters connected on Modbus RTU network and where the Omron FB is too memory hungry.<br />Reads <u>upto</u> 16 registers from register 20 and writes to two registers (Fixed at 1 and 2). <br /><br />Set the serial port to Serial Gateway and set the baud rate to match the inverters. Inverter default is 81N. In the V1000 set H5-01 to the address. It must start at 1 and have no gaps.<br />The baudrate works upto 115200 (with V1000)<br /><br />Data format suits V1000 F7 E7. Don't use for V7 or J7.<br /><br />Data is only written on a change. The change is managed in the PLC NOT in the inverter. Data is read sequentially from node 1 to 'MaxNodes'.<br /><br />Not tested on CP1L-L (one serial port version). I think its Easy modbus addresses are different to two port versions.<br /><br />You can choose addresses within CIO only.<br /><br />Refer to any inverter manual for modbus addresses. Edit: the CP1L 14/20 use port two EasyModbus addresses. I think you can select Port 2 but set port 1 to Serial Gateway. Can someone try this?? Submitter ParaffinPower Submitted 03/09/2008 Category PLC Sample Code 2
mAriC Posted July 22, 2009 Report Posted July 22, 2009 hi , lot thanks for FB. first i try with CP1L 2port PLC and its works very well. but with cp1L-L 1port its not working. i try change port numbers and with &2 plc something send and vfd recive messages but plc not recive messages, and recive data table is empty. 1
2431 Posted April 2, 2020 Report Posted April 2, 2020 Hi, the output from serial port 2 is in modbus format? can i use this fb to operate Yaskawa V1000 VFD?, and how can we use this block to operate multiple vfds
2431 Posted April 2, 2020 Report Posted April 2, 2020 On 3/9/2008 at 9:40 PM, ParaffinPower said: File Name: CP1L and CP1H EasyModbus FB File Submitter: ParaffinPower File Submitted: 9 Mar 2008 File Category: PLC Sample Code Ideally suited to multiple Omron inverters connected on Modbus RTU network and where the Omron FB is too memory hungry.<br />Reads <u>upto</u> 16 registers from register 20 and writes to two registers (Fixed at 1 and 2). <br /><br />Set the serial port to Serial Gateway and set the baud rate to match the inverters. Inverter default is 81N. In the V1000 set H5-01 to the address. It must start at 1 and have no gaps.<br />The baudrate works upto 115200 (with V1000)<br /><br />Data format suits V1000 F7 E7. Don't use for V7 or J7.<br /><br />Data is only written on a change. The change is managed in the PLC NOT in the inverter. Data is read sequentially from node 1 to 'MaxNodes'.<br /><br />Not tested on CP1L-L (one serial port version). I think its Easy modbus addresses are different to two port versions.<br /><br />You can choose addresses within CIO only.<br /><br />Refer to any inverter manual for modbus addresses. Edit: the CP1L 14/20 use port two EasyModbus addresses. I think you can select Port 2 but set port 1 to Serial Gateway. Can someone try this?? Click here to download this file Could you please share PLC sample code, i am unable to find here. how can i use this block (Inverter Refresh the only FB in attachment) ?
Janaka Angampitiya Posted June 14, 2020 Report Posted June 14, 2020 On 3/9/2008 at 10:10 PM, ParaffinPower said: File Name: CP1L and CP1H EasyModbus FB File Submitter: ParaffinPower File Submitted: 9 Mar 2008 File Category: PLC Sample Code Ideally suited to multiple Omron inverters connected on Modbus RTU network and where the Omron FB is too memory hungry.<br />Reads <u>upto</u> 16 registers from register 20 and writes to two registers (Fixed at 1 and 2). <br /><br />Set the serial port to Serial Gateway and set the baud rate to match the inverters. Inverter default is 81N. In the V1000 set H5-01 to the address. It must start at 1 and have no gaps.<br />The baudrate works upto 115200 (with V1000)<br /><br />Data format suits V1000 F7 E7. Don't use for V7 or J7.<br /><br />Data is only written on a change. The change is managed in the PLC NOT in the inverter. Data is read sequentially from node 1 to 'MaxNodes'.<br /><br />Not tested on CP1L-L (one serial port version). I think its Easy modbus addresses are different to two port versions.<br /><br />You can choose addresses within CIO only.<br /><br />Refer to any inverter manual for modbus addresses. Edit: the CP1L 14/20 use port two EasyModbus addresses. I think you can select Port 2 but set port 1 to Serial Gateway. Can someone try this?? Click here to download this file Please send me your .cxp file. I don't know how to use this FB function.
IO_Rack Posted June 15, 2020 Report Posted June 15, 2020 The links were broken some time ago. Here it is. Please post questions in the Omron Forum.
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now