i''ve been creating a modbus TCP network on Omron. i 've get CP1W-modtcp61 adapter but CX-Programmer is not have it. so i'm finding how to update cx-programmer but always appear : " fail to authenticate " , i need help update or find CP1W-MODTCP61.cxp .
You do not need to find it in CX-Programmer. You configure it from an HTML page when you plug into the module. From the PLC's perspective, it looks like a serial connection. The Modbus TCP module converts Modbus TCP to serial to communicate with the PLC. Follow the instructions in this manual: CP1W-MODTCP61_SetupGuideManual_EN_201207.pdf
  • Like 1
http://s749.photobucket.com/user/painzstyle/media/Modbus_zpsceb15a4f.png.html ( view this ) when i enter to" IO table andd Unit Setup" , i can't insert adapter CP1W-TCP61 , because i need to configure a modbus TCP network . Edited by Irelia
Again, the module DOES NOT show up in the I/O table. Those 2 slots are only for CJ1 modules that are connected to the side of a CP1H. If you look under settings in the project workspace, you will see serial port 1 and 2. These are the slots that the module plugs into. You will NOT see the module there either though. Section 2 in the manual that I attached shows you how to configure the Port settings as well as set dip switches. It then goes not to describe how to do the HTML configuration.
