Jump to content

Recommended Posts

Posted
I'm having trouble communicating with my PLC. I have an CQM1H-CPU11, I'm using a USB-CN226 cable. I installed the driver that came with the cable. If I try to go online, it pops up "Failed to connect to the PLC." My dip switches are currently in the the positions of 1 off, 2 off, 3 on, 4 off, 5 off, 6 off, 7 on, 8 off. Any help would be greatly appreciated!
Posted
Dipswitch 5 is off which means serial settings according to user setup, if you don't know these I suggest to put dipswitch 5 to on and select Toolbus, 9k6, 7,e,2 in CX-Programmer. CQM1 Dipswitches.pdf
Posted
I changed the dipswitch 5 to on, and I had no change.... The pic of the "PLC Change with Network Settings [Tool Bus]" I'm not sure how to pull that up? The CX-Programmer Version I'm using is 9.0. I've checked the Device Manager on my PC for the driver and there doesn't seem to be any problems there... Is there any thing else I can try?
Posted
Well setting Dipswitch 5 on alone is not enough, you have to make sure the settings are as in the picture, and select the correct COM port. To pull up the settings see below picture.
  • Like 1

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Restore formatting

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...