Jump to content

Recommended Posts

Posted
Hello there. I have connected wireless module (master) to Vijeo Citect 7.4 using RS-485 to USB converter. My slave modules are supplied power from gird/generator and the master module is supplies from a UPS. 
 
I'm reading Modbus registers of slaves modules data via wireless master. Every time we have a power failure from grid, I get #BAD from all slave addresses. The generator kicks off within 30 sec. That is the slaves are off for 30 sec. Even after the slaves are powered on, SCADA does not poll data from it until I restart the SCADA. 
 
My current MODBUS parameters are:
 
Inittype = 3,
TimeOut = 3000,
WatchTime = 10,
Retry = 2.
Could you please assist me on which parameters to change in .ini so that SCADA reads Modbus registers of slave for more than 30 sec.
 
I tried increasing TimeOut to 30000 but it couldn't solve the problem. I would appreciate if some one could help me out.
 
Thanak you in advance.  
 
 

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Restore formatting

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...