Bruno1 Posted November 24, 2017 Report Posted November 24, 2017 (edited) I have a question regarding the need for a control power transformer in a control panel. I have a 230VAC 3 phase control panel that I'm designing. I need 110VAC in that panel for various items. Is there any reason why I can't pull the 110VAC directly from one of phases on the distribution block (fuse it of course) and the neutral side from the neutral distribution block rather than installing a control power transformer? I've seen other designs where in similar cases a control transformer (230VAC to 110VAC) was used. Does it have to do with separately derived neutrals or is the transformer not even necessary? Thanks Edited November 24, 2017 by Bruno1
Mendon Systems Posted November 24, 2017 Report Posted November 24, 2017 If it was powered by 208Y then no problem, but 230 comes in various flavors depending on where you are located. Some 230 sources have a neutral reference that provides 115 volts and others don't. There is also the infamous "wild leg" 230 that has one phase which is at 284 volts to the neutral. It is a whole lot safer to use a 230/120 control transformer.
Bruno1 Posted November 24, 2017 Author Report Posted November 24, 2017 The project is in the Northeast. I was mistaken on my original post, the supply is 230 VAC single phase. So I can easily get 110VAC from that. What are the rules as to when a control transformer is required? Thanks again for the help.
nehpets Posted November 24, 2017 Report Posted November 24, 2017 Personally, I would go for 230v to 110v centre tapped to earth, this would reduce the touch voltage to 55v (unless of course you are dull enough to touch the two legs at the same time ), this is a much safer option. Steve
IO_Rack Posted November 24, 2017 Report Posted November 24, 2017 If the main breaker is a GFI then using the neutral will cause it to trip.
nehpets Posted November 25, 2017 Report Posted November 25, 2017 Oops I didn't make it very clear that the 110v would be derived from an isolating transformer 230v primary / 110v secondary centre tapped to earth. Steve
IO_Rack Posted November 25, 2017 Report Posted November 25, 2017 You were clear enough. I was responding to Bruno1 with a situation were a control transformer would be required.
cHud Posted November 28, 2017 Report Posted November 28, 2017 (edited) We often supply cabinets where our supply is prone for spikes. Using a control transformer reduces the damage that can be caused to the control side ( power supply or coil etc side). That is our main reason for installing them. If history is a yard stick then I wouldnt go without them in a 3 phase to single phase or 24vdc control cabinet. Even when supplied by single phase. Might be an overkill but doing things proper results in less problems. Often don't know the state of customers electical supply until there is a fault in your cabinet Edited November 28, 2017 by cHud
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now