LEMON FOAM Posted June 10, 2019 Report Posted June 10, 2019 I'm new to Mitsubishi PLC programming. I want to communicate my Q13UDEHCPU (Q-series PLC CPU) and GT2308-VTBA (GOT2000 HMI) by using the built-in Ethernet port on the 2 devices Picture 1 to 3 shown the setting in the GOT2000 HMI using GT-Designer program, Picture 4 shown the setting in the PLC CPU using GX-Work program Picture 1: I/F Communication Setting Picture 2: Controller Setting Picture 3: GOT Ethernet setting Picture 4: Built-in Ethernet port Setting Beside than the setting in the 4 pictures, is there any other setting i need to do so that the 2 devices can communicate via built-in Ethernet port Quote
DaMro Posted June 11, 2019 Report Posted June 11, 2019 I think that problem is because of setting same station number for Got and PLC. Please change GOT station number to 40. Quote
LEMON FOAM Posted June 12, 2019 Author Report Posted June 12, 2019 (edited) 18 hours ago, DaMro said: I think that problem is because of setting same station number for Got and PLC. Please change GOT station number to 40. Sir, what u mean by same station no? Is it the same IP address? So i need to set the IP address for GOT at picture 3 to 192.168.3.40 and set the IP address for PLC in picture 4 to 192.168.3.39? But why i need to set them as 40 and 39? Because when i see from the Mitsubishi manual, it set the IP address for GOT and PLC as 18 and 39 Beside than that, in the manual it had stated that setting in PLC side is not needed. Edited June 12, 2019 by LEMON FOAM Quote
LEMON FOAM Posted June 13, 2019 Author Report Posted June 13, 2019 (edited) On 6/12/2019 at 2:47 PM, DaMro said: I marked point which you should change. Sir, u mean i need to set the PLC and GOT into different station? Beside than that, am I needed to set the IP address port no to different value as shown in the picture below? Edited June 13, 2019 by LEMON FOAM Quote
DaMro Posted June 13, 2019 Report Posted June 13, 2019 Yes, you need to set different stations numbers. For IP adress you need to set them into same group: 192.168.3.***. For example: PLC: 192.168.3.39 GOT: 192.168.3.18 By the way, if you have clean PLC and GOT, you don't have to change anything in PLC parameters and in GT-Designer it is enough to select correct Controller type and connection type. All other settings should stay defaults. Quote
LEMON FOAM Posted June 13, 2019 Author Report Posted June 13, 2019 11 minutes ago, DaMro said: Yes, you need to set different stations numbers. For IP adress you need to set them into same group: 192.168.3.***. For example: PLC: 192.168.3.39 GOT: 192.168.3.18 By the way, if you have clean PLC and GOT, you don't have to change anything in PLC parameters and in GT-Designer it is enough to select correct Controller type and connection type. All other settings should stay defaults. I see, thank you for ur explanation. As conclusion, if we need to connect PLC and GOT by built in ethernet port, we need to set them into different station and IP. Am i right? And what did u mean a clean PLC and GOT, is it a new PLC and GOT? Quote
Recommended Posts
Join the conversation
You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.