Jump to content

Recommended Posts

Posted (edited)

Can anyone tell me if there's a rule in NFPA79 consistent with UL508A 60.1. Basically 60.1 states that a main disconnect is not required in an industrial control panel IF the size and type of protection are and clearly stated and that a disconnect is required by the installer, noted on the electrical drawings.

Edited by Bruno1
Posted

NFPA79 chapter 5 talks about the incoming power connection and disconnecting means. Section 5.3 covers the disconnecting means. I'm not 100% sure what you mean, but I don't see many exceptions to the requirement to provide a supply circuit disconnecting means within the enclosure except for panels that are smaller than 2HP and they need one close by and clearly identified. I didn't read the whole section, though.

Posted

NFPA79 : 5.1.9.6

Each machine disconnect means other than attachment plugs and receptacles shall be mounted within the control enclosure it supplies OR IMMEDIATELY ADJACENT THERTO. 

I have one machine that I do not include the disconnect means, the customer/installer must provide the disconnect. And I put this in big letters on my drawings..

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Restore formatting

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...