Hello,
I need to make communication NB TW01B by Omron with Siemens's S7 1200 PLC using MODBUS TCP. I did everything like in this manual:
https://www.myomron.com/index.php?action=kb&article=1566
I can read and write single bits from and to DB but I have problem with representation of float variable.
In hmi_variable.png you can see my DB. Every BOOL variable communicate just fine the real ones doesnt.
In NB - variables.png you can see how i added them into NB panel variable table.
Settings.png shows settings of my INPUT number element on the frame( screen in NB).
When I write on panel for example number 10.0 then from the panel view it looks properly but in PLC you can see value like in the 10.0.png.
What am I doing wrong? Any suggest?
Edited by owerel209
https://support.industry.siemens.com/tf//WW/en/posts/send-real-floating-values-to-client-with-modbus-tcp/144597?page=0&pageSize=10
" Note also that Modbus only works with 16-bit registers, so transferring a REAL value (32-bit IEEE format) will require you to send 2 contiguous Modbus registers and reassemble them as REAL values in your partner "
In the PLC are you putting together the two 16 bit registers and then interpreting them as a float?
I would look at inputting the integer number and decimal number separately on the HMI. Then use the PLC to interpret the data.
Just a thought.
Regards,
Garry
My target was to make value with decimal number representation. I already achieved this by sending INT type multiply by 10 and in options "numeric data" changed its representation: integer 2 , decimal 1. Thank you for answers.
