as1988 Posted September 10, 2021 Report Posted September 10, 2021 PLC: Mitstubishi FX3G 24MR/ES There is 220VAC coming to the PLC supply pins, but no indication LEDs are switched on and there is no 24VDC service supply. This PLC is used to control the sauna. Before dismantling PLC, is it possible that there is some unmet condition that is preventing PLC from starting? For example, if Emergency stop is activated and wired to the PLC input, can it prevent PLC from starting? Just a reminder, there is 220VAC at the L and N pins of the PLC.
Gambit Posted September 10, 2021 Report Posted September 10, 2021 you are supplying 24V to the terminals below, but these already provide 24V!!!!
as1988 Posted September 10, 2021 Author Report Posted September 10, 2021 42 minutes ago, Gambit said: you are supplying 24V to the terminals below, but these already provide 24V!!!! It is not outside 24VDC that are being supplied to the PLC. 24VDC are supplied by the PLC and then distributed further - it is, so called, service power supply.
Gambit Posted September 10, 2021 Report Posted September 10, 2021 ok than maybe there is a short, only connect the power on top L/N. If the power LED doesn't turn on the unit is broken.
as1988 Posted September 10, 2021 Author Report Posted September 10, 2021 2 hours ago, Gambit said: ok than maybe there is a short, only connect the power on top L/N. If the power LED doesn't turn on the unit is broken. Ok, thank you.
Ron_S Posted September 10, 2021 Report Posted September 10, 2021 The 24 vdc is not normally wired like that. It's not good practice to parallel supply's.
as1988 Posted September 11, 2021 Author Report Posted September 11, 2021 21 hours ago, Ron_S said: The 24 vdc is not normally wired like that. It's not good practice to parallel supply's. There is just one 24VDC power supply and it is the PLC's service power supply.
Ron_S Posted September 11, 2021 Report Posted September 11, 2021 (edited) Well all the outputs are being supplied by it. The plc 24vdc is very low amps. Go over that and the supply shuts down. Edited September 11, 2021 by Ron_S
glavanov Posted September 13, 2021 Report Posted September 13, 2021 (edited) When 24V service power suply of Fx series is overloaded or short circuit the green power and red error leds are solid ON. Program led OFF. and you can see the error by GXW2 with PLC diagnostics function. It happened to me with Fx3U, not sure for Fx3G series. Problem might be elsewhere... PLC AC-DC converter, blown AC fuse or, AC line... Edited September 13, 2021 by glavanov
as1988 Posted September 15, 2021 Author Report Posted September 15, 2021 On 13/09/2021 at 0:23 PM, glavanov said: When 24V service power suply of Fx series is overloaded or short circuit the green power and red error leds are solid ON. Program led OFF. and you can see the error by GXW2 with PLC diagnostics function. It happened to me with Fx3U, not sure for Fx3G series. Problem might be elsewhere... PLC AC-DC converter, blown AC fuse or, AC line... Thank you, much appreciated.
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now