kckku Posted September 17, 2021 Report Posted September 17, 2021 Why am I getting this message when trying to synchronize with the NA HMI? What does 'PLC has not been validated' mean? 2021-09-17_14-11-55.bmp
photovoltaic Posted September 17, 2021 Report Posted September 17, 2021 Never seen this one - did you upload the PLC and the HMI? Perhaps you could share the Sysmac project file?
kckku Posted September 17, 2021 Author Report Posted September 17, 2021 15 minutes ago, photovoltaic said: Never seen this one - did you upload the PLC and the HMI? Perhaps you could share the Sysmac project file? I tried uploading with a new auto connect project. I then made the changes that I wanted to make to the uploaded HMI. Tried to synchronize again and got the same message. It's also telling me that the RunTime on the HMI is newer than the one on my computer. Not sure why this is a problem but maybe related? Also noticed the PLC only exists on one side when trying to synchronize. 2021-09-17_14-35-45.bmp 2021-09-17_14-37-23.bmp
photovoltaic Posted September 17, 2021 Report Posted September 17, 2021 I can't recreate it unfortunately. Did you try forcing the runtime download?
BobB Posted September 17, 2021 Report Posted September 17, 2021 4 hours ago, kckku said: I tried uploading with a new auto connect project. I then made the changes that I wanted to make to the uploaded HMI. Tried to synchronize again and got the same message. It's also telling me that the RunTime on the HMI is newer than the one on my computer. Not sure why this is a problem but maybe related? Also noticed the PLC only exists on one side when trying to synchronize. 2021-09-17_14-35-45.bmp 2021-09-17_14-37-23.bmp Sounds like you need to update studio.
Crossbow Posted September 20, 2021 Report Posted September 20, 2021 The only PLC that requires validation is the NX Safety CPU. Did you enable the Safety Monitor in the HMI Settings? In order to use this, the safety CPU must be in a validated state. This will add a check box on the Synchronize screen for Safety Data.
kckku Posted September 20, 2021 Author Report Posted September 20, 2021 (edited) 2 hours ago, Crossbow said: The only PLC that requires validation is the NX Safety CPU. Did you enable the Safety Monitor in the HMI Settings? In order to use this, the safety CPU must be in a validated state. This will add a check box on the Synchronize screen for Safety Data. Yes, I did enable the safety monitor function in the HMI. The safety PLC hasn't been changed though so I am not sure why this is a problem all of a sudden. I am only trying to upload the HMI program so I can add a user alarm. If I am using the safety monitor, then I have to check this box to also synchronize the safety data? I got a screenshot when I try to synchronize to the HMI. There is a box for 'Safety Data'. 2021-09-20_13-50-29.bmp Edited September 20, 2021 by kckku Added screenshot
Crossbow Posted September 20, 2021 Report Posted September 20, 2021 The safety project in the open project has to match the one in the controller, and the controller must be in its validated state. The safety data in the HMI is tied to a validated safety controller. If you're trying to upload, then don't pick the safety data, that is a download thing...
kckku Posted September 20, 2021 Author Report Posted September 20, 2021 1 hour ago, Crossbow said: The safety project in the open project has to match the one in the controller, and the controller must be in its validated state. The safety data in the HMI is tied to a validated safety controller. If you're trying to upload, then don't pick the safety data, that is a download thing... @Crossbow I did a complete upload from the controller and got the safety PLC program as well. Previously I didn't upload the safety PLC program so this is what caused the not validated error when I tried to synchronize the HMI (with the safety monitor option selected). Thanks for helping to solve this. Now I am still seeing a RunTime mismatch. What does this mean exactly? I attached a screenshot. What is the date format? YYYY/MM/DD or YYYY/DD/MM? I had to update the RunTime in the HMI before to get the safety monitor option to work. The HMI was previously running an older RunTime (1.11) which didn't have the safety monitor function. Now it's running RunTime 1.15. 2021-09-20_17-22-02.bmp
Crossbow Posted September 22, 2021 Report Posted September 22, 2021 Do a build on the project (hit F8), then synchronize the project, and check if it goes away.
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now