Jump to content

Recommended Posts

Posted

Theoretically....maybe. I've worked on HMI migrations where I had old and new operating side by side and it went ok...on the bench. But I wouldn't try to do so in the field. Having two devices control the same thing is generally not a good idea.

Posted
7 hours ago, Joe E. said:

Theoretically....maybe. I've worked on HMI migrations where I had old and new operating side by side and it went ok...on the bench. But I wouldn't try to do so in the field. Having two devices control the same thing is generally not a good idea.

Thank you sir, i will use a different address

Posted

I have seen one case where this was done.  The PLC had a tag "Motor_Start_PB"  and each HMI was configured to toggle on "Motor_Start_PB" but never to hold it on or turn it off.

The PLC code then at the end of scan had an Unlatch Motor_Start_PB if it was on.

This worked, but you never knew which station started the machine.

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Restore formatting

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...