MZohaib92 Posted June 8, 2022 Report Posted June 8, 2022 Hi,I want to read transducer signal on PLC.I am using 7kg60008ab/nn transducer and it's analog (4-20mA) output is connected with analog meter.Can I connect the transducer current output (4-20mA) signal to PLC analog input in series with analog meter display???So that I can read the value on PLC simultaneously with analog meter? Quote
pturmel Posted June 9, 2022 Report Posted June 9, 2022 If the analog input on the PLC is isolated/differential, then yes, you can route the loop through the PLC between transmitter and meter. 1 Quote
MZohaib92 Posted June 9, 2022 Author Report Posted June 9, 2022 (edited) 2 hours ago, pturmel said: If the analog input on the PLC is isolated/differential, then yes, you can route the loop through the PLC between transmitter and meter. I have Fatek PLC FBs-6AD . Its datasheet shows " Isolation- Transformer(Power) and photo-coupler(Signal)" https://smartdk.com/SmartFTP/Fatek/Manualer/FBs_6AD_Datasheet_en.pdf Edited June 9, 2022 by MZohaib92 Quote
pturmel Posted June 9, 2022 Report Posted June 9, 2022 (edited) The wiring diagram in that document suggests that each input is differential and isolated. The manual doesn't say that is the case, but it looks like it. You'll have to try. I would expect it to work. Neither the power nor photo-coupled signal isolation indicate that the input terminals themselves are channel-to-channel isolated or isolated from ground. Edited June 9, 2022 by pturmel Quote
