Jump to content

Recommended Posts

Posted (edited)

This module is intended to be used as a DeviceNet slave gate to DVP-Slim series DI/DO or special (AI/AO, temperature, loadcell) right-side extension modules. It could be coupled with  DVPDNET-SL DeviceNet module. DVPDNET-SL is a left-side module for DVP-Slim series PLCs. Unlike RTU_DNET it could be used as both master and slave. This way users could built a high speed network.

Configuration software used is called DeviceNet Builder and could be downloaded freely from Delta's Download center. RS-485 configuration is set by the path Setup-> Communication setting-> System communication port and then <serial port setup> window from the configuration software menu. Both modules could be setup using the same software.

 

The RTU-DNET application manual posted above should be used. DVPDNET-SL operation manual is located here:

https://filecenter.deltaww.com/Products/download/06/060305/Manual/DELTA_IA-PLC_DVPDNET-SL_OM_EN_20230906.pdf

 

Edited by IvanBratanov
  • Like 1
Posted

With the resources I linked, you now know as much as I about this combination.  The documentation obviously is oriented towards scanning this DeviceNet slave from a Delta PLC--you'll have to re-interpret that yourself to conform to Kuka's requirements as the master.  I don't know anything about that.

You will certainly need a PC to DeviceNet hardware interface compatible with the software for that RTU in order to configure it.  I assumed you understood that, but maybe not.

  • Like 1
Posted (edited)
On 22.05.2024 г. at 9:44 PM, mehrandinio@gmail.com said:

 

I have a master module on the Kuka robot…

 

As I mentioned above DVPDNET-SL module can not work remotely or separately, i.e. it must be coupled with a DVP-S series PLC. I deeply doubt that KUKAs are controlled by such PLCs so you have to couple the DVPDNET-SL to a DVP-SA2 PLC for example first. Then you have to configure both devices to work together. Then you have to connect the KUKA’s automation to the SA2 PLC in order to send and receive data to/from the DEVICENET network. The SA2 has built-in one RS-232 and two RS-485 ports supporting MODBUS ASCII and RTU protocols. If the robot’s automation doesn’t support such interfaces you have to add a coresponding left-side module to the SA-2 PLC. In this case the PLC should interact as s gateway between both interfaces. For example if the robot supports PROFIBUS, you should attach and configure a DVPPF02-SL left-side module to the SA2 PLC. 
I don’t believe that using third-party automation together with such devices as KUKAs is a good idea because of the complications and difficulties you have to go thru first. 

Edited by IvanBratanov

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Restore formatting

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...