jdolecki Posted July 18, 2024 Report Posted July 18, 2024 I have three PF525 I need to wire the STO pins. Is it acceptable to wire all them in parallel to the safety relay out. Or does each drive need its own relay output? Thanks
pturmel Posted July 18, 2024 Report Posted July 18, 2024 2 minutes ago, jdolecki said: wire all them in parallel IIRC, this will function, but reduces the safety classification in most cases. If the upstream relay is physically two separate relays in series internally, with appropriate failure interlocking, it may be acceptable. If the upstream safety relay provides paired solid-state outputs, parallel connection would almost certainly not be acceptable. Without a risk assessment, I wouldn't do it.
jdolecki Posted July 18, 2024 Author Report Posted July 18, 2024 The risk assessment say all motion must stop if e stop is pushed. My Kinetex5100 servo manual shows the safety inputs in series for multiple drive to STO so I assumed this was the same for the PF. So I assumed this was acceptable for the PF 525 but they would have to be paralleled. what do I know
pturmel Posted July 19, 2024 Report Posted July 19, 2024 Yeah, somehow I missed the multiple PF525 situation. I thought you wanted to feed S1 and S2 on one PF525 from a single circuit. But this: 6 hours ago, jdolecki said: The risk assessment say all motion must stop if e stop is pushed. Is a very simplistic risk assessment. It doesn't address the level of faults that must be accepted with still-working safety stop.
BobLfoot Posted July 19, 2024 Report Posted July 19, 2024 The manufacturer documentation you show is very clearly labelled "Coast with TWO Powerflex drives". I would not assume it can be applied to THREE without checking with Rockwell Technical Experts. There is the possibility that the Relay Output cannot support more than two drive input units. If there is a "coast with MULTIPLE Pwoerflex Drives" example then I would be much more comfortable with doing what you're asking from a single relay.
VFD Guy Posted July 20, 2024 Report Posted July 20, 2024 11 hours ago, BobLfoot said: The manufacturer documentation you show is very clearly labelled "Coast with TWO Powerflex drives". I would not assume it can be applied to THREE without checking with Rockwell Technical Experts. There is the possibility that the Relay Output cannot support more than two drive input units. If there is a "coast with MULTIPLE Pwoerflex Drives" example then I would be much more comfortable with doing what you're asking from a single relay. Looks to be a cascade configuration. I wouldn’t focus on 2 vs multiple
BobLfoot Posted July 20, 2024 Report Posted July 20, 2024 18 hours ago, VFD Guy said: Looks to be a cascade configuration. I wouldn’t focus on 2 vs multiple yes and each drive draws 6ma. 1
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now