Jump to content

Omron NS10-TV01B-V2 showing black screen and bottom right corner "Connecting..."


Recommended Posts

Posted

Omron NS10-TV01B-V2 showing black screen and bottom right corner "Connecting..." when validate project showing pop up message "There is file name against the rule delete the setting and saves" and couple of overlap object warning. Need help where file name against the rule? 

 

Snag_2a20f97d.png

Snag_2a210eda.png

Posted

I've never seen this error before.

Did you perform a download with this error?

1) "Connecting..."    generally means the PLC communications settings are not set properly.

2) For the validation error, I would check any external files the project may be using. For example, an Indirect Reference of String. Make sure the file name is simple. No special characters and using 8 characters or less.

Posted

Thank You for response. I created a simple one-rung PLC project and a new HMI project. After downloading it to the HMI, it still shows the same "Connecting..." error. All PLC and HMI IP settings appear to be correct, and the test simulation with the PLC is working perfectly. System version and Project version is 8.90

I called Omron tech support waiting on their call back. 

Snag_2f5cc5a6.png

Snag_2f5cffd1.png

Snag_2f5e4dad.png

Snag_2f5f02b5.png

Posted

When do you receive the error message?

If it's during validation, I would guess the problem is in your CX Designer installation. I would update it if you haven't already, re-install and/or try on another PC.

If for some reason you believe the issue is in the PT, go to the Initialize tab from the system menu and initialize all data areas.

I don't know that any of these actions will solve the issue but these are things I would try. Hopefully Omron tech support can shed some light on it.

Posted

Can you show the plc setup? 

What CPU do you have?  Not all CPU's support eth/ip

Have you tried FINS instead of ethernet/ip?

From memory the tag needs to be set to network publish to be able to access.

 

 

Posted

For FINS you'll need to set the PLC network with CX-Integrator as I don't believe the NS supports network 0. For EIP you'll need to setup the tags in the CX-Programmer Symbols section - check off "Net. Variable:" and leave as publication to make a variable accessible for EIP.

Posted
46 minutes ago, Javid Musa said:

Thank You all. I got Omron support doing this it fix the issue. Transfer host from serial A to Host3 and delete Serial A host 

Snag_349514dd.png

Snag_34953853.png

So your actual issue was your symbols created in the symbol table. Doing what Omron suggested would have updated your tags to point to the correct host. Your tags you created must have been selected to "SERIALA".

See below.

CommSettings.thumb.png.2438eb4fb787f6624SymbolTable.thumb.png.8f8ab5f0353c8fb230

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Restore formatting

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...