Jump to content

Tia portal uploaded project without tags


Go to solution Solved by Hati,

Recommended Posts

Posted

Hi

I uploaded tia portal v13 project from ET200S cpu, the uploaded project now is without tags.

i asked engineers and the answer was that: during project downloading ,the tags stay in original project file, not downloaded to s7 300/400 families CPUs.
Now all the tag names are useless in this project as they are not downloaded to cpu.
So will it be problem for compile and re-download the uploaded project back to cpu?
Will it be OK for hmi to communicate with plc using absolute addressing only?

I don't have the original project files of both HMI and PLC


Thanks


Posted (edited)
On 3/26/2025 at 1:38 AM, Swissi said:

Hi

I uploaded tia portal v13 project from ET200S cpu, the uploaded project now is without tags.

i asked engineers and the answer was that: during project downloading ,the tags stay in original project file, not downloaded to s7 300/400 families CPUs.
Now all the tag names are useless in this project as they are not downloaded to cpu.
So will it be problem for compile and re-download the uploaded project back to cpu?
Will it be OK for hmi to communicate with plc using absolute addressing only?

I don't have the original project files of both HMI and PLC


Thanks Poor bunny !

It’s true that S7-300/400 CPUs don’t store tag names, only memory addresses. If the logic is intact, you should be able to compile and download without issues. As long as the HMI uses absolute addressing, communication should work fine. However, troubleshooting and modifications may be harder without the original tag names. Consider documenting the addresses to avoid further confusion. Good luck!

Edited by MarlonLane
Posted

Hi

Thanks for explanation 

 As the cpu uses absolute addresses, does it mean also the hmi uses absolute addresses ??

Regards 

  • Solution
Posted
2 hours ago, Swissi said:

Hi

Thanks for explanation 

 As the cpu uses absolute addresses, does it mean also the hmi uses absolute addresses ??

Regards 

Yes, the HMI also uses absolute addressing when the CPU is 300/400 series.

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
×
×
  • Create New...