Jump to content

Recommended Posts

Posted (edited)

 

Hello,

I have a problem with communication between PLC NX102 and SCADA Zenon via CIP. I use 3400 variables in the project and two monitors. A large number of them are displayed or used in trends. So there are lags in refreshing variables. I increased the time of refreshing variables in SCADA, but the communication is still too slow. After reviewing the communication in WireShark, the longest times in communication occur on the PLC side. It takes about 70ms for the PLC to respond to SCADA. If I had set Task Period in Sysmac Studio to 2ms, it took 150-250ms to respond, now I have set Task Period to 10ms. Further increasing Task Period does not affect the communication speed.

The response time of 70ms is normal, can it be shortened somehow?

Edited by mati99.94

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Restore formatting

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...