Jump to content

Recommended Posts

Posted
hi all, i need a urgent favor from u all. what is the limitation addressing for MP 370 by using S5? i have two type of addressing to use, 1) P linear 2) Q linear P Linear have addressing conflict for S5 but i have to use it and Q Linear might not be compatible with the S5. Please suggest that which is better to be use?or is there any other method to be slove? thanks in advanced to u all. best regards, sun367
Posted
Hi there... I believe P and q are some sort of adressing range.... but i am not so sure ... this settings have to be set on the COM Profibus setting for IM308-c. Ok the best thing i give you the whole scenario... S5 CPU115-U communicating to a MP370 through an IM308-C. what i have tried: there is an option tiny (32 inputs and 22 outputs), small (42 inputs and 22 outputs), medium (64 inputs and 32 outputs) and finally big (122 inputs and 64 outputs). i chose middle and followed all the settings for middle from the PLC S5 program to the Protool Program. but i still have some error. Please advice... thanks a million, Ivan
Posted
Have you used the standard Fb supplied by Siemens to control the MP when connected via DP? I think it is FB58 and it requires a DB as well? Hope it helps

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Restore formatting

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...