Jump to content

Recommended Posts

Posted
Hi all, I am new to Siemens PLC...So need help regarding I/O redundancy... The system is CPU 414-4H with redundant I/Os on IM 153-2, means if the first IM module has one DI module at slot 4 (address 0,1), then the second redundant IM module also has one DI module at slot 4(address 2, 4). the signal coming from field will go to the same channel of both the DI module. Now my problem is : If PLC is getting a Digital input from field at I0.0 and same is wired to I2.0 And if I want to use this signal in PLC programming, do i have to AND/OR both the DI i.e. I0.0 & I2.0? Or simply using I0.0 will solve the problem...? If second IM module is acting as a active module then using DI I0.0 will work? Please help if somebody know about this. Regards & best wishes, Prashant Yelattiwar

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Restore formatting

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...