Jump to content

Recommended Posts

Posted (edited)
Loadcell voltage is too low for PLC analog input. A signal conditioner/amplifier is required. It's unclear from the link provided whether the loadcell is with or without amplifier. Also, what is the resolution of the A/D converter? 8-bit resolution may be insufficient (only 256 increments). Edited by Sergei Troizky
Posted
The FX2N-4AD is capable of reading in 4-20 mA which is equivalent to 0 - 1000 bits, giving a resolution of 16 mA equivalent to 1000 bits. It can also read in a 0-10 volts signal, but in this case, I believe the resolution drops as I'm pretty sure that the range -10 to +10 volts is equivalent to 0 - 1000 bits. You can really improve the resolution by investing in an FX2N-8AD module and setting it so that 0 - 20 mA is equivalent to 0 - 20,000 bits, giving resolution to one thousandth of a mA. However, as Sergei rightly says, without knowing what signal the load cell gives out (which is unclear from the PDF) it's not possible to say how to connect it to the analogue input module, or what the resolution would be. I get the impression a phone call to the load cell manufacturers might be a good idea?

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Restore formatting

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...